Barry Kann
Member
- Location
- United States
In a residence, when a 120V-10A heater is on, 1.5A flows in the Grounding Electrode Conductor (GEC). I isolated the current to the ground in the old unused copper telephone cable. Since there is no connection at all to this cable, I disconnected this phone ground from the GEC. The 1.5A in the GEC went away. The phone cable ground was providing a parallel path for neutral current. Who caused the problem, the phone company or the utility company?
Barry Kann
Fox Mill Electric Service
Barry Kann
Fox Mill Electric Service