Jmad757
New member
- Location
- Chesapeake,va,usa
So I got a 200amp 3phase 120/208 meter with a fused disconnect with rk5200a 200000 fuse and a 200 amp 10000 aic panel ... Max fault current is 59000 ..are my fuses good for let thru current ???
The fuses would not need to be "good for let thru", they just need to have an AIC rating at or higher than the Available Fault Current, which yours do. Let-through it what gets PAST the fuses to the devices down stream before they clear a fault.So I got a 200amp 3phase 120/208 meter with a fused disconnect with rk5200a 200000 fuse and a 200 amp 10000 aic panel ... Max fault current is 59000 ..are my fuses good for let thru current ???