Anyone aware of a current limiting device for a lighting circuit serving a pendant light. Not track lighting. Energy code related.
I see current limiting sub panels available, nothing for one circuit only.
Anyone aware of a current limiting device for a lighting circuit serving a pendant light. Not track lighting. Energy code related.
I see current limiting sub panels available, nothing for one circuit only.
My limited knowledge of current limiting has to do with various power supplies I have in my shop. They put out variable voltages either AC or DC and are current limiting. They have a current sensing circuit that limits the amount of output current no matter what the load impedance is. If you short the output the current drops to 0.
It is a very user friendly feature for clutz's like myself![]()
Of course, a current limiter panel like this is overkill for OP's application --
210.3 Rating. Branch circuits recognized by this article
shall be rated in accordance with the maximum permitted
ampere rating or setting of the overcurrent device. The rating
for other than individual branch circuits shall be 15, 20,
30, 40, and 50 amperes. Where conductors of higher ampacity
are used for any reason, the ampere rating or setting
of the specified overcurrent device shall determine the circuit
ra
On the other hand I think it is perfect. The OP mentions he could use 10 amp branch circuit breakers to accomplish his goal.
I do not believe the NEC allows 10 amp branch circuit so running each 20 amp branch circuit through a current limiter panel should take care of it.
An individual branch circuit powers a single piece of equipment. Could you consider the track and its installed luminaires a single piece of equipment, since it is a (field assembled) unit connected to a single outlet on the house wiring?The rating
for other than individual branch circuits....
An individual branch circuit powers a single piece of equipment. Could you consider the track and its installed luminaires a single piece of equipment, since it is a (field assembled) unit connected to a single outlet on the house wiring?
Branch Circuit, Individual. A branch circuit that supplies
only one utilization equipment.
On the other hand I think it is perfect. The OP mentions he could use 10 amp branch circuit breakers to accomplish his goal.
I do not believe the NEC allows 10 amp branch circuit so running each 20 amp branch circuit through a current limiter panel should take care of it.
That was a good explanation. From an electronic point of view I have one of those dual power supplies that does that. I just had to change hats from electric power distribution to electronics. With electrical stuff sometimes it's a challenge to make sure that everything is within its withstand and interrupting rating when a short circuit occurs. As such you often have to rely heavily on CL fuses and circuit breaker to coordinate with down stream devices and their series ratings.
Templdl
wow, you fired a spark in my thinking! Yes CLF fuses which we work around in dist switchgear all the time limit the fault current (current limiting) to usually 1/4 cycle of the sine wave. I recall class J, Bussmann KTK control fuses with an IRC / IAC rating of 200KA, and power fuses with ratings.....??? Not much utility LV fault current is above 200,000A, at least in the SF CA bay area.
They all have their purpose to contol the electron flow during a fault
When people ask what I do, I tell them I'm in Electron Management, which pretty much covers it all
Tony
I think you're mixing up this thread with another one: http://forums.mikeholt.com/showthread.php?t=154334