alsafaj
Member
- Location
- Dubai, UAE
The purpose is to sense and trip the breaker for ground fault. The graph is not clear to me............Hello,
For an IDT 132 kV, a primary value of a CT is given at 3200 A -- A trigger is set for a residual or neutral current at 8% for the HV side. I would like to understand the purpose and how to read this out from the below graph.
View attachment 18927
Thank you,
The purpose is to sense and trip the breaker for ground fault. The graph is not clear to me............
From the graph, there appears to be several positive peaks which exceed 200A (8% out of balance) but being only positive and no negative, a DC offset is being introduced into the system somewhere. Another question I have is whether that 8% is from system 0 volts or a calculated expected neutral current. The latter will require vector math and compensation for nonlinear loads.Suppose trigger value of 8% is set at 1500A of neutral current i.e at 120A. In your case the actual neutral current has a maximum value of 117.5A only. So the breaker would not trip. You may have to reduce the trigger value for that.
From the graph, there appears to be several positive peaks which exceed 200A (8% out of balance) but being only positive and no negative, a DC offset is being introduced into the system somewhere. Another question I have is whether that 8% is from system 0 volts or a calculated expected neutral current. The latter will require vector math and compensation for nonlinear loads.
This is a calculated expected In (trigger setting in primary 120 A)
Looking at the graph, I was able to see the maximum current is about 224.1 A prior to trigger activation .. Once triggered I saw the value dropped at 204.7 which's > 8% but drop. Isn't this supposed to be overcurrent trigger.
I am confused. What am I missing here?
The trigger value 120A is RMS value and not peak value and 117.5A is also RMS value. Otherwise the breaker would have tripped at peak values of 224.1A or 204.7A. Did it?
alsafaj: Your problem is the breaker should not trip under the given conditions but it trips-fault violation. Correct?