Desk Jockey
New User
- California
- Green Energy
I am attempting to close out a PV farm and have encountered a problem that I am unable to solve. I have a high circulating current at the concentric neutrals on all Photovoltaic and Battery Storage MV circuits at the (2) substations we have on site. Our 3rd party testing contractor was on site and recorded values from 30A to 100A at 60Hz. The current is not constant, it will hold for a short period of time and then disappear, “almost like a pulse” according to the NETA tech. Some MV circuits had current on all (3) phases and others only on individual phases, the specific individual phase with current varied from circuit to circuit. (5) MV junction boxes were tested and produced the same results, 19A to 85A. Measurements were also taken at (1) inverter but the results were less than 1A on each phase.
Approximately (3) weeks ago, an MV junction box suffered a fault at the C phase deadbreak connector, we believe it to be due to a loose connection. During the circuit inspection, it was discovered that multiple Cold Shrink tubes located at the base of the deadbeak connector in multiple MV junction box locations had failed. The Cold Shrink had either split up the side and hung from the cable or completely fell off. My concern is that this is related to heat created by the circulating current found on the concentric neutral and the potential to damage other terminations. Any ideas?