A bit of a mystery here.
An A/C unit has 2.7 A of current on the condenser pipes that run from furnace to the outside unit.
1.8 A on the big, 0.9 A on the small one.
Happens whenever the gas furnace is running, even with AC off.
There is 2.7 A of imbalanced current on the circuit supplying the furnace (means I am clamping around entire cable which should not have a reading if current in and out was equal), and also 2.7 A on the circuit supplying the A/C unit (which has the breaker off).
There is 2.6 A on the EGC in j-box on the furnace, this EGC terminates at furnace enclosure/casing.
L has 8.9 A and N has 8.6 A when furnace is running. No current on gas pipes.
3 ft of heat tape is coiled around PLASTIC box and 2 ft of plastic drainage pipe. No shorts to ground on it.
No metal is touching the heat tape. It has an extension cord to a recep on the same circuit as furnace.
The moment I unplug the heat tape, no more amps on the condenser pipes... Goes down to 0.04 A
Trying to remove the current from the pipes where it's not supposed to be (no voltage to ground on the pipes).
Could there be a metal piece or pipe inside that plastic box the heat tape is coiled around, creating induced current that runs on the EGC onto the enclosure, and from there, takes a loop on the condenser pipes (possibly amplified by the internal coils on the AC)?
Any ideas about cause and cure?
An A/C unit has 2.7 A of current on the condenser pipes that run from furnace to the outside unit.
1.8 A on the big, 0.9 A on the small one.
Happens whenever the gas furnace is running, even with AC off.
There is 2.7 A of imbalanced current on the circuit supplying the furnace (means I am clamping around entire cable which should not have a reading if current in and out was equal), and also 2.7 A on the circuit supplying the A/C unit (which has the breaker off).
There is 2.6 A on the EGC in j-box on the furnace, this EGC terminates at furnace enclosure/casing.
L has 8.9 A and N has 8.6 A when furnace is running. No current on gas pipes.
3 ft of heat tape is coiled around PLASTIC box and 2 ft of plastic drainage pipe. No shorts to ground on it.
No metal is touching the heat tape. It has an extension cord to a recep on the same circuit as furnace.
The moment I unplug the heat tape, no more amps on the condenser pipes... Goes down to 0.04 A
Trying to remove the current from the pipes where it's not supposed to be (no voltage to ground on the pipes).
Could there be a metal piece or pipe inside that plastic box the heat tape is coiled around, creating induced current that runs on the EGC onto the enclosure, and from there, takes a loop on the condenser pipes (possibly amplified by the internal coils on the AC)?
Any ideas about cause and cure?