190526-0847 EDT
mbrooke:
A TT is two single phase transformers.
The primary current of a single phase transformer is approximate determined by the transformer turns ratio times the secondary current.
The wild leg current is straight forward. The other currents have to be determined by phasor addition.
https://en.wikipedia.org/wiki/Scott-T_transformer
.
From the outside looking in, it is a Delta-Wye transformer. The primary and secondary conductors and OCP can't tell any different.How to calculate for code wire sizing and primary OCPD? Nothing in Mike Holts material.
190526-0847 EDT
A TT is two single phase transformers.
From the outside looking in, it is a Delta-Wye transformer. The primary and secondary conductors and OCP can't tell any different.
As for the currents in the coils and the winding conductor sizes, that is up to the xfm mfg to size to meet spec
Yes; read gar's wiki link.So that means if all currents are equal on the secondary, the will be equal on the primary?
What I find fascinating is the way it can be used to transpose 3ph to 2ph or 2ph to 3ph. Wow. I must read more.
Yes; read gar's wiki link.
I did note that when I read the entire page. My comment still stands, correct equipment used.No.
It takes a somewhat special Scott-Tee connection to go between 3ph and 2ph. A standard run of the mill T connection is strictly 3ph to 3ph.
You can tell the difference by looking at the position of the taps on the windings.
1905226-2221 EDT
In a wild leg 3 phase connection what is the phase angle between the voltage of the X1-X3 single phase winding, and the X2-CT voltage? It is 90 degrees. That is fundamentally a 3 phase to 2 phase converter. A Scott T.
A T-T configuration is basically one Scott T converter driving a second Scott T in reverse. Taking 3 phase to 2 phase and 2 phase back to 3 phase.
Take Wiki with some question. Do your own analysis. Wiki has a lot of correct discussion and information.
.
190527-0959 EDT
Tony S:
You have drawn a standard Scott T for 3 phase to 2 phase. That which is the first Wiki drawing. The Wiki drawing is better than yours because it provides a somewhat intuitive impression of the phase angle relationships.
I believe that mbooke's original question relates to the second Wiki circuit, 3 phase to 3 phase. It is probably referred to as a T-T because it is really two Scott Ts in series. A different layout of the schematic might make this clearer.
.
From the outside looking in, it is a Delta-Wye transformer. The primary and secondary conductors and OCP can't tell any different.
As for the currents in the coils and the winding conductor sizes, that is up to the xfm mfg to size to meet spec
So that means if all currents are equal on the secondary, the will be equal on the primary?
Yep - unless the mfg is doing something strange and not telling us.
Draw a box around the transformer and just look at the vectors. They will look like a delta primary and a wye secondary.
Direct observation (as in empirical data) - and opinion:
Outfits that are buiding these, are doing so because they can save a buck-46 on copper and steel (or aluminum/steel in this case). And the xfm tend to run really hot, as in too hot to touch. Which wasn't really part of the question - but perhaps interesting