2 Gen sets connected to a 3-pole Xfer switch. 3-phase 4 wire with EGCs..
One gen set is bonded ( G-N).. The other is not. 250.20(d) fpn.1.
The Xfer switch feeds an MDP.. MDP feeds around 8 SDPs.. SDPs feed trailers.. EGC run w/all feeders from trailer all the way back to gen.
I have approximately .5 to 1,2 amps on each EGC that is run w/each SDP feeder cable that terminates at the MDP .. I have approximately 8 amps from MDP to Xfer switch.. and 8 amps on EGC from Xfer to Gen. ( the gen set that is running )..
When I disconnect all 8 EGCs coming from the SDPs at the MDP it reduces the current from the MDP to Xfer switch to 3 amps.. I also still have 3 amps from Xfer switch back to the gen set.. There are no bonding jumpers in the trailers or anywhere else in the system.. I cant find any leaks to ground at the trailers..When all EGCs are disconected from the MDP why do I still have 3 amps going back to Gen ? Is that current coming FROM the bond at the gen set and using the Xfer switch and MDP as another source to ground ? Is my grounding electrode resistance at the genset too high so its looking for a lower resistance path ? I have moved the EGCs away from phase conductors as much as possible to avoid induction.. any thoughts ? :-?
One gen set is bonded ( G-N).. The other is not. 250.20(d) fpn.1.
The Xfer switch feeds an MDP.. MDP feeds around 8 SDPs.. SDPs feed trailers.. EGC run w/all feeders from trailer all the way back to gen.
I have approximately .5 to 1,2 amps on each EGC that is run w/each SDP feeder cable that terminates at the MDP .. I have approximately 8 amps from MDP to Xfer switch.. and 8 amps on EGC from Xfer to Gen. ( the gen set that is running )..
When I disconnect all 8 EGCs coming from the SDPs at the MDP it reduces the current from the MDP to Xfer switch to 3 amps.. I also still have 3 amps from Xfer switch back to the gen set.. There are no bonding jumpers in the trailers or anywhere else in the system.. I cant find any leaks to ground at the trailers..When all EGCs are disconected from the MDP why do I still have 3 amps going back to Gen ? Is that current coming FROM the bond at the gen set and using the Xfer switch and MDP as another source to ground ? Is my grounding electrode resistance at the genset too high so its looking for a lower resistance path ? I have moved the EGCs away from phase conductors as much as possible to avoid induction.. any thoughts ? :-?