Current on GEC

Status
Not open for further replies.

DBoone

Senior Member
Location
Mississippi
Occupation
General Contractor
The meter at my home is mounted on the utility pole beside my driveway. The GEC exits thru the bottom of the meter and is bonded to the GEC running down the side of the utility pole. So from the meter to the transformer is a parallel path for neutral current. Several weeks ago I checked with my meter and had 3 amps on my GEC. If one was to disconnect the meter GEC from the utility GEC and then hold one in each hand would they receive a shock? Thanks.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Assuming that there are no problems with the service grounded conductor, then the only voltage that would across the open GEC would be the voltage drop on the service grounded conductor and that should not be enough to cause a shock hazard. If there is a problem with the service neutral, there will be shock hazard.
 