just the cowboy
Inactive, Email Never Verified
- Location
- newburgh,ny
Hey guys
I went to check a compressor that tripped a breaker last week, did normal checks megged motor all seemed ok.
Reset breaker and started compressor started no problems, checked current a=188 b= 190 c= 194 current around all three was .3 amps maybe. Looked good, I checked the current on the ground wire coming into the disconnect to the compressor and had 3.8 amps on the ground wire. This got me because I have never seen that much on the ground wire, checked both wires that were under the bonding lug one had 3 amps one had .8 amps showing me current was flowing on conduit also I guess.
Shut off compressor and current went away, I thought great motor problem. Fired up a second compressor and had same thing only more current on that ground. Fired up third compressor more current on ground. Now I know I don't have three bad compressors.
They are the only thing on this 1500a panel. We have two services feeding the building both are 13.2kv/480v wye/wye. The compressors are 100 hp. 150 hp. and 200 hp. I see 11-18 amps on what I think is the bonding jumper from neutral to ground in the switchgear and it don't have any 277 loads. This is a new building just built.
Can this much current just be induced I have never seen that much current on ground wire in 40 years.
Thoughts
I went to check a compressor that tripped a breaker last week, did normal checks megged motor all seemed ok.
Reset breaker and started compressor started no problems, checked current a=188 b= 190 c= 194 current around all three was .3 amps maybe. Looked good, I checked the current on the ground wire coming into the disconnect to the compressor and had 3.8 amps on the ground wire. This got me because I have never seen that much on the ground wire, checked both wires that were under the bonding lug one had 3 amps one had .8 amps showing me current was flowing on conduit also I guess.
Shut off compressor and current went away, I thought great motor problem. Fired up a second compressor and had same thing only more current on that ground. Fired up third compressor more current on ground. Now I know I don't have three bad compressors.
They are the only thing on this 1500a panel. We have two services feeding the building both are 13.2kv/480v wye/wye. The compressors are 100 hp. 150 hp. and 200 hp. I see 11-18 amps on what I think is the bonding jumper from neutral to ground in the switchgear and it don't have any 277 loads. This is a new building just built.
Can this much current just be induced I have never seen that much current on ground wire in 40 years.
Thoughts