A water supply company has two pumps moving water to fill the reservoir.
The complaint reports that each motor has a problem and they are different problems. The 150HP trips on unbalanced current. The 600HP is going out on ground trip. A PQA was connected on the 150HP and a recording was taken.
No motor testing has been done since the plant was built two years ago.
The water company is measuring small continuous currents on the ground bonds when one of the motors was running but not when both were running, which does not happen often.
The question here is; there was a recording Fluke 345 meter on the grounding conductor at the 150HP switchgear when it started. The grounding conductor had a 25A+ during startup. The recordings are being reviewed and the water company will be doing more test.
Both motors are 480Y/277VAC with soft starts.
What can cause the ground currents?