Re: Current on grounding conductor
3 Amps on a grounding electrode is not very much and if the electrode is a commonly connected water main then it's common to even have more. This is because current takes all paths back to source not just the one with the least resistance. A water main will be in parallel with with your service neutral as well as your neighbors service neutral and you will see current from both services flowing on the GEC, A grounding electrode can pass as much as 4.8 amps if it has the NEC minimum of 25 ohms resistance to Earth, but this would be proportional to the amount of unbalanced current on the service neutral and could indicate a week or lost neutral. The third possibility is the transformer supplying your service or one just down the road has lost it's primary neutral (MGN) and is now getting it's return path through your service grounding electrode system, in this latter case it should be mention that if you opened your grounding electrode connections at your service you could find yourself with primary voltage on your service grounding so you should never remove all grounding electrode connections if you suspect a bad primary neutral. The utility will come out and check the neutral for you by seeing if there is any current on their primary neutral, if there is not any current on it, then they know that it's getting a return from somewhere else, If you have both a water pipe electrode and a rod or other type of electrode removing the water pipe connection should cause the current and voltage to Earth to rise, if this happens then call the utility immediately! Of course put the connection back ASAP. And wear HV gloves when doing this test. Under no reason disconnect the other type of electrode! as it will be the only thing keeping the voltage at bay. Also turn off all the single pole breakers on one leg of the panel so if there is a lost neutral it can't fry anything but it will still apply a load to the transformer.