I would like advice on the following issue we have in our neighborhood, specifically my home. I will describe the test we have done and the results, then ask for advice.
For one, I cannot understand how this is allowed to happen from a code stand point. More importantly, how do I correct this problem and stay within code. I see proposed solutions, but it seems to me I need to go through the proper channels to make sure I am in compliance with local codes. Do I talk to the power company, water company, and/or building inspector?
Additional, I wonder what the effect of this situation is if my home is supplied by a different transformer that my neighbors home?
Thank you
- We shut off the main breaker to my home
- We shut off the main breaker to my neighbors home across the street
- We placed a clamp meter no my neutral line
- We read 0.2 amps
- We then turned on my neighbors power
- Next we turned on two hair dryers creating 28 amps on his supply line
- His neutral line clamp meter read 23 amps
- My neutral line clamp meter read 5 amps
- This same test done in reverse created the exact same but opposite results
- This same test done with homes adjacent to my home did not add amps to my neutral line
- With this test, we create 5 amps running on the water pipe, therefore we are able to walk the water pipe using a Gauss meter
- The water pipes of our two homes must be connected to the main very close to each other
For one, I cannot understand how this is allowed to happen from a code stand point. More importantly, how do I correct this problem and stay within code. I see proposed solutions, but it seems to me I need to go through the proper channels to make sure I am in compliance with local codes. Do I talk to the power company, water company, and/or building inspector?
Additional, I wonder what the effect of this situation is if my home is supplied by a different transformer that my neighbors home?
Thank you