bjohnson
Member
- Location
- North dakota
This is a carryover from the old forum.
Quick rehash on the problem:
The waterline coming into my house has up to 5 amps on it. This continues through the ground wire to the panel to the grounded condutor on the service entrance. I've opened the main breaker to verify that the source was not from within the house or caused by an unbalanced load on the conductors and confirmed that the source was not from within my house. Also note that there was no current on the water pipe after the clamp for the ground wire and no current on any of the house piping. The current varies with it typically highest during the evening. My house is located closest to a pole mounted transformer.
My hypothesis is that one of my neighbors has a loose connection on their grounded conductor and thanks to Mr. Kirchoff, a portion of that current is returning to the transformer via the water pipe and my connection.
The city Electrical Inspector is at least showing an interest and contacted the POCO and relayed the information. The POCO came to the house to look. Unfortunately I was not there at the time and they only took readings on the conductors and chalked it up to the imbalance between the two. and came to my house to verify I knew what I was talking about. I also showed him the EMF readings from my gaussmeter that followed nicely along the waterline. The last word on the topic was that inspector wanted to study up on it a bit more and he'd get back to me.
My questions is about how to remedy the situation. The way I see it so far is one of four options: 1) Find the neighbor with the problem and tighten/troubleshoot the connection. Easiest and probably what I'll do. Any tips would be appreciated. 2) Install a dielectric couple on the waterline after the 10 foot point to satisfy the NEC requirements. The main drawback is this would require either cutting the concrete floor in my basement or digging 8+ feet in my front yard. 3) Disconnect the ground clamp. Not very good since there could potentially be a potential on the water pipe and under the right (wrong?) circumstances cause problems. 4) Do nothing.
EMF wise the basement has a linear field following the water pipe. On the floor the levels have been in excess of 50 mG (meter pegged). 3 feet off the ground will range from 10 to 30 mG. On the floor above readings were >5mg.
I will note that my gaussmeter is not known for accuracy. (Cellsensor)
And if Mr Riley is watching, I'd like to commend him on his book 'Tracing EMF's in building wiring and grounding'. I found it very informative.
[ February 26, 2003, 01:00 PM: Message edited by: bjohnson ]
Quick rehash on the problem:
The waterline coming into my house has up to 5 amps on it. This continues through the ground wire to the panel to the grounded condutor on the service entrance. I've opened the main breaker to verify that the source was not from within the house or caused by an unbalanced load on the conductors and confirmed that the source was not from within my house. Also note that there was no current on the water pipe after the clamp for the ground wire and no current on any of the house piping. The current varies with it typically highest during the evening. My house is located closest to a pole mounted transformer.
My hypothesis is that one of my neighbors has a loose connection on their grounded conductor and thanks to Mr. Kirchoff, a portion of that current is returning to the transformer via the water pipe and my connection.
The city Electrical Inspector is at least showing an interest and contacted the POCO and relayed the information. The POCO came to the house to look. Unfortunately I was not there at the time and they only took readings on the conductors and chalked it up to the imbalance between the two. and came to my house to verify I knew what I was talking about. I also showed him the EMF readings from my gaussmeter that followed nicely along the waterline. The last word on the topic was that inspector wanted to study up on it a bit more and he'd get back to me.
My questions is about how to remedy the situation. The way I see it so far is one of four options: 1) Find the neighbor with the problem and tighten/troubleshoot the connection. Easiest and probably what I'll do. Any tips would be appreciated. 2) Install a dielectric couple on the waterline after the 10 foot point to satisfy the NEC requirements. The main drawback is this would require either cutting the concrete floor in my basement or digging 8+ feet in my front yard. 3) Disconnect the ground clamp. Not very good since there could potentially be a potential on the water pipe and under the right (wrong?) circumstances cause problems. 4) Do nothing.
EMF wise the basement has a linear field following the water pipe. On the floor the levels have been in excess of 50 mG (meter pegged). 3 feet off the ground will range from 10 to 30 mG. On the floor above readings were >5mg.
I will note that my gaussmeter is not known for accuracy. (Cellsensor)
And if Mr Riley is watching, I'd like to commend him on his book 'Tracing EMF's in building wiring and grounding'. I found it very informative.