Current per phase

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
on a 2500 kva 480y/277 transformer we calculated approx 3007 amps, the question is, "Are these 3007 amps per each phase or combined over all 3 phases?
What formula did you use to make the calculation?

The three phase power formula most commonly used gives you the magnitude of the current in each of the three lines.
This is NOT the same as the current in each of the three phases (line to line).
It is certainly not the sum of the magnitudes of the three line currents.
 

Fnewman

Senior Member
Location
Dublin, GA
Occupation
Sr. Electrical Engineering Manager at Larson Engineering
In commonly used terms, 3007 amps would be the secondary current for each phase of a 2500 kVA 3 phase transformer. It a number that you would often find on the nameplate.
 

Smart $

Esteemed Member
Location
Ohio
that would make sense it is per phase thank you
NO.

It is commonly but errantly stated as amps per phase. The correct terminology is line amperes.

This particular aspect of a transformer is known as the rated primary or secondary current.
 