If I have 30A, 2-pole breaker feeding a 10 Horsepower, static phase converter that feeds a 21A, 230V, 3-phase motor; what is the current at the breaker on each of the two poles?
Something is wrong here.Wow. I wonder if it would have been better to get a transformer and run it at 460V. I also read on the eBay seller's page that the output isn't truly 3-phase power and that it runs at reduced horsepower. When I checked voltage I got 240V from A-B and B-C but nothing from C-A. Each phase to ground was 120V. I plan on amprobing the wires to see for sure. I also see some guys online recommend a VFD or run a 3-phase motor with a single-phase motor and couple them. BTW, this is for a lathe.
I wonder if the so called 'static phase converter' is actually the set of components that would ordinarily be used to get a rotary phase converter spinning.
A rotary phase converter is just a three phase induction motor. Two legs are connected to your supply, and when the motor is spinning the third leg is generated by the motor. To get the motor spinning some sort of phase shift network is used, such as capacitors. Usually this network gets disconnected by a contactor.
This same sort of system could be used to spin a motor; apply single phase two two legs plus a phase shifted third leg, get the motor going, and then disconnect the motor, leaving it spinning 'single phased'.
If you have a link to the auction page, perhaps we can figure out more.
-Jon
No way to know an absolute number, because the LOAD determines the current drawn by your motor, not the rating. The 21A FLC just tells you the MAXIMUM current the motor can safely draw, not what it ACTUALLY draws.
No way to know an absolute number, because the LOAD determines the current drawn by your motor, not the rating. The 21A FLC just tells you the MAXIMUM current the motor can safely draw, not what it ACTUALLY draws.
But whatever current is drawn by the motor based on the load it is connected to, will be increased by a factor of 1.732 on the input side of your phase converter, plus any inherent losses in the converter (which we also don't know). So of your 3 phase motor current is 10A, the current drawn from your 1 phase supply will be 17.32A, but only if your converter is 100% efficient, which never happens. If you assume worst case scenario, that the converter is 80% efficient, then the current drawn will be 21.65A (17.32/.8).
Hope that helped you.