current sensing
jinglis
Ontario
I would like to monitor the current on an 8 gauge wire (one leg of a 120/240 volt feed) and I have no idea how to go about it or what is on the market to make this a simple task. I would like this current to trip a relay or two relays at two different settings ( 5 amps and 25 amps ). Any ideas.
You could use two current sensing relays on the same line each set with it's own trip point.
This one runs on 240, provides contacts but is only adjustable from 2 to 20 amps. However with a little searching I bet one with a 25 amp trip point could be found.
(image and link deleted by gbynum)
following your link, then to the manufacturer's site, I find http://www.ssac.com/catalog/ECS01A01.pdf where many options exist ... including a 5-50 range.
Re the followup question on more current than ratings ... the electronics would probably saturate and do ok; the CT would probably overheat. IF you really need that Grainger stocked unit, 2 parallel conductors with a little intentional resistance to force load sharing should do with one through the ct, one not.