A few months ago we replaced the Coal Crusher motors at one of our plants, the nameplates match up the same as the old ones, nothing has changed the motors were just really old. We are seeing occasional current spikes that we were not seeing before. It makes sense to me that we would see occasional spikes just because of it being a crusher motor and there can be larger/harder pieces that get tossed in to be crushed, but the spikes we are seeing are above and beyond what we have seen in the past, and the HP and Torque rating of the motor matches the motor that it replaced. Any ideas?
Currently we have a high alarm at 111A (the Full Load Amp rating on the nameplate) and a high-high alarm at 115A. The DCS requires amps to drop by 4A to clear the alarm. Is there a recommendation that anyone here has for the high alarm above nameplate amps? Just wondering what others are used to seeing and if they've had to make adjustments to their DCS system for their crusher motors as well. Appreciate any insight.
Currently we have a high alarm at 111A (the Full Load Amp rating on the nameplate) and a high-high alarm at 115A. The DCS requires amps to drop by 4A to clear the alarm. Is there a recommendation that anyone here has for the high alarm above nameplate amps? Just wondering what others are used to seeing and if they've had to make adjustments to their DCS system for their crusher motors as well. Appreciate any insight.