Hello all! I have a question regarding current harmonics. I have an AC drive (Siemens SM150) feeding four AC motors (1070 KW, 3300 V each) that is injecting current harmonics to the system at 2900 V. I have modeled it in SKM as a lump load and added a harmonic library to it. This load has a current THD of 20.9%. I do not have any other harmonics sources in the entire model and I do not have any filters in the model. I only have two reactors say M1 and M2 below the utility (13.8 KV). When I do harmonic analysis for the whole system and try to look harmonics at the PCC, I see that M1 has (going through) a TDD% of 54%. I do not understand how this level went so high when all I have is one harmonic source in the entire system.
If this can happen, how do I bring current TDD below IEEE 519 limit? As I already have two reactors, what else can I do to bring the harmonics down without impacting the system? Thank you.
Note: 1. Voltage harmonics (THDv) is under limit and is looking good.
2. I do not have exact demand factor for the loads so I assumed that all the loads are connected and running.
If this can happen, how do I bring current TDD below IEEE 519 limit? As I already have two reactors, what else can I do to bring the harmonics down without impacting the system? Thank you.
Note: 1. Voltage harmonics (THDv) is under limit and is looking good.
2. I do not have exact demand factor for the loads so I assumed that all the loads are connected and running.