How about a description. A CT allows a large current to be read indirectly using a representational current, so the meter need not carry the actual current. The meter's readout must be matched to the CT for accurate measuring.
A typical CT with, say, a 400:5 ratio, which is the same as 80:1, has 80 turns in the secondary, so, for each amp in the single conductor passing through the 'donut", there is 1/80 of an amp through the meter, or 1 amp in the meter for each 80 load amps.
Note that the CT's secondary circuit is of almost zero impedance, as most ammeters are, so little voltage is developed; it's all current. However, if this circuit is opened, the CT now functions as a PT (potential transformer), with a step-up ratio of 1:80.
An extremely high voltage can be developed with just a small amount of primary current. Usually, the first damage is to the insulation of the secondary winding from arcing, but external arcing can also occur, along with personnel hazards.