I have always known that a current tranformer's secondary winding is NOT to left open circuited under no circumstances under load as it will burn out,I am hearing rumours that there is a current transformer that will not ? can someone clear the air?
Well i dont know about burning out i dont see how it would but a ct left open under load is a dangerous condition of high voltage potential we usally short them out when around these . take care best to ya
Well i dont know about burning out i dont see how it would but a ct left open under load is a dangerous condition of high voltage potential we usally short them out when around these . take care best to ya
An unterminated CT acts like a PT and reverses the CT's current ratio. A 400:5 CT, with an 80:1 turns ratio, can act as a 1:80 PT. The result can be thousands of volts in what is now the secondary.So they burn up if left open never have i seen one ever after were done left open on any job.
Rogowski Coil current sensors don't burn up if open circuited. They are available, but I haven't seen very many - don't know why not. As I understand, the concept is 70+years old, but they weren't practical until the electronics bcame available.
One would have expected them to become popular after the electronic relays started coming out.