dan55
Member
- Location
- South Dakota
I am trying to determine if a current transformer is working or not. should there be voltage at the leads that terminate at the meter.
charlietuna said:good advice, but understand most new current transformers have resistors across the secondary to prevent high voltage buildup.
. Standard secondary current should be 5Amp but in some new designs 1Amp. at full primary current ie 800:5 or 1600:5[/QUOTE said:If it's an 800:5 or 1600:5 CT , why would the secondary current only be 1 amp at full primary ?
djohns6 said:That's a VERY broad statement and I disagree .
I'm not sure I understand your question, but . . .djohns6 said:If it's an 800:5 or 1600:5 CT , why would the secondary current only be 1 amp at full primary ?
LarryFine said:I'm not sure I understand your question, but . . .
When a CT is operated with the secondary open, it behaves like a PT. A 400:5 CT has an 80:1 current ratio, but a 1:80 PT.
That can damage the CT as well as surrounding equipment and people.
djohns6 said:A previous post stated that an 800:5 CT might have 1 amp secondary current at full primary load ( 800 amps ) . I was asking for an explanation of that . :smile:
BTW , I've seen the firerworks that an open CT can produce . Luckily I was about 30 feet away .
weressl said:I think what he meant to say is that there are CT's that have 800:1, in other words CT's with a 1A secondary rating.
Having said that, the 1A rating in the US is not a standard CT rating like the universally accepted 5A is/was. Rather manufacturers of formerly 'solid state' and now 'electronic' trip devices, either integral or separate, have developed proprietary current sensors with lover current rating that are more suitable to interface with electronic circuitry.
Didn't I say that? :smile:dereckbc said:Not to over do the subject but current and voltage are inversely proportional. I have worked in the utility biz as a sub station engineer earlier in my career and a standard CT used in 345 KV substations is 600:1 . Ok what that means is the voltage ratio is 1:600 . . .
LarryFine said:When a CT is operated with the secondary open, it behaves like a PT. A 400:5 CT has an 80:1 current ratio, but a 1:80 PT (ratio).
LarryFine said:Didn't I say that? :smile:
dereckbc said:Not to over do the subject but current and voltage are inversely proportional. I have worked in the utility biz as a sub station engineer earlier in my career and a standard CT used in 345 KV substations is 600:1 . Ok what that means is the voltage ratio is 1:600 so if you were to open a CT on a active line, and it has been done, the voltage can go to 207 MV. I knew a few relay techs and substation switch operators that accidently opened them. Only one survived if that is what you want to call it.
dereckbc said:I have worked in the utility biz as a sub station engineer earlier in my career and a standard CT used in 345 KV substations is 600:1 . Ok what that means is the voltage ratio is 1:600 so if you were to open a CT on a active line, and it has been done, the voltage can go to 207 MV. I knew a few relay techs and substation switch operators that accidently opened them. Only one survived if that is what you want to call it.
Well . . . :roll:roger said:Oh, and like you have never posted something someone else had. :grin:
So I'm excused, since I'm not a member of The Mod Squad.beanland said:I am concerned that a "moderator" can make this large an error.