I am taking a role in which I have a large role in the design of a custom dual VFD panel and I'd like some sound advice before I proceed. So this is a 3-phase panel for controlling 8 fan motors at the load but that is beside the point. The feeder breaker of 150A splits to (2) 100A breakers, so I have to split the wires on the output side of the 150A breaker at some point before the 100A breakers. I have a distribution block which will accommodate #3/0 from the 150A breaker to the block but the output side has 4 outputs per phase but max out at #2AWG each. The #2AWG wire is on the verge of the ampacity rating of 100A for the slave breakers. Will this pass an UL inspection if #2AWG THHN wire is used from the block to the 100A breakers? THHN is rated at 90 deg so 130A correct??
Also an unrelated question: On a distribution block or breaker would it be ok to put multiple conductors into a sleeve that combine to the less than the max wire size for that terminal? For example; with a circular terminal of a max of 400mcm wire size, would it be ok to insert (2) #1AWG (84MCM each equiv.) wires into a sleeve and then insert it into the terminal?
Also an unrelated question: On a distribution block or breaker would it be ok to put multiple conductors into a sleeve that combine to the less than the max wire size for that terminal? For example; with a circular terminal of a max of 400mcm wire size, would it be ok to insert (2) #1AWG (84MCM each equiv.) wires into a sleeve and then insert it into the terminal?