Can someone please confirm my thinking? Here's the situation:
Large industrial facility w/ multiple buildings. Buildings are fed by customer-owned MV overhead distribution and pad mount transformers. Each pad mount transformer has its own ground ring, and each building has its own grounding electrode system.
Two questions:
1. Are the underground service conductors (conductors between XFMR secondary and main service disconnect) required to have a ground conductor run with them?
2. If a ground conductor is installed with the service conductors, would it technically be considered a "supply side bonding jumper"?
My guess is that a ground conductor is not required with the service conductors as long as there's a neutral (grounded conductor, technically), and the neutral is bonded to ground at both the transformer and main disconnect. Is this correct?
Thanks in advance!