Customer Owned MV XFMR - Is Sec. Ground Conductor Required?

Status
Not open for further replies.

Sunny_92

Member
Location
York, PA
Occupation
Electrical Engineer
Can someone please confirm my thinking? Here's the situation:

Large industrial facility w/ multiple buildings. Buildings are fed by customer-owned MV overhead distribution and pad mount transformers. Each pad mount transformer has its own ground ring, and each building has its own grounding electrode system.

Two questions:

1. Are the underground service conductors (conductors between XFMR secondary and main service disconnect) required to have a ground conductor run with them?

2. If a ground conductor is installed with the service conductors, would it technically be considered a "supply side bonding jumper"?

My guess is that a ground conductor is not required with the service conductors as long as there's a neutral (grounded conductor, technically), and the neutral is bonded to ground at both the transformer and main disconnect. Is this correct?

Thanks in advance!
 
Last edited:

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Can someone please confirm my thinking? Here's the situation:

Large industrial facility w/ multiple buildings. Buildings are fed by customer-owned MV overhead distribution and pad mount transformers. Each pad mount transformer has its own ground ring, and each building has its own grounding electrode system.

Two questions:

1. Are the underground service conductors (conductors between XFMR secondary and main service disconnect) required to have a ground conductor run with them?

2. If a ground conductor is installed with the service conductors, would it technically be considered a "supply side bonding jumper"?

My guess is that a ground conductor is not required with the service conductors as long as there's a neutral (grounded conductor, technically), and the neutral is bonded to ground at both the transformer and main disconnect. Is this correct?

Thanks in advance!

It looks like under the 2017 NEC, the supply-side bonding jumper would not be required if the installation is made in compliance with 250.30(A)(1) Ex. No. 2.
 

jumper

Senior Member
It looks like under the 2017 NEC, the supply-side bonding jumper would not be required if the installation is made in compliance with 250.30(A)(1) Ex. No. 2.

Is it the same as the 2014?

Exception No. 2: If a building or structure is supplied by a
feeder from an outdoor transformer, a system bonding
jumper at both the source and the first disconnecting means
shall be permitted if doing so does not establish a parallel
path for the grounded conductor. If a grounded conductor
is used in this manner, it shall not be smaller than the size
specified for the system bonding jumper but shall not be
required to be larger than the ungrounded conductor(s).
For the purposes of this exception, connection through the
earth shall not be considered as providing a parallel path.
 

Sunny_92

Member
Location
York, PA
Occupation
Electrical Engineer
Thanks for the responses, it looks like we're in agreement with regard to the 2014 & 2017 code.

How about here in PA where we're under the 2008 code? It looks like a "supply-side bonding jumper" was formerly referred to as an "equipment bonding jumper," and 250.30(A)(2) doesn't seem to require it. Is a supply side equipment bonding jumper required by 250.102?
 

ron

Senior Member
The OP makes reference to "underground service conductors", I don't think that the secondary of a customer owned MV - LV transformer results in "underground service conductors".


The secondary is just a feeder that needs to be in compliance with 240.21(C).

Just like any feeders from the secondary of a transformer that is a SDS, it needs to have a a SSBJ run with it if the N-G bond is at the XFMR.
 

publicgood

Senior Member
Location
WI, USA
The specific reference is:

250.32 Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s). (B) Grounded Systems. (1) and (2).

No separate equipment grounding conductor, just the SSBJ.
 

Sunny_92

Member
Location
York, PA
Occupation
Electrical Engineer
So to summarize, in this situation, the requirements for a "supply-side bonding jumper" are the same in the 2008 NEC as they are in the 2014 & 2017 NEC, except the wording/terminology is much clearer in the later editions.

Does anyone disagree?
 