Thought I’d share this one.
I did the wiring installation for the hot tub 14/yrs ago while the pool was still under construction. The original HO worked for the tub manufacturer, which is why they didn’t do a built in spa.
Anyway, new HO calls me, they feel voltage entering and exiting the spa. They’ve lived here 4/yrs and this just started.
Here are pics of install
I.
Pool water to pool deck = 0v
Pool deck to stairs = 0v
Spa water to stairs = 2v
Spa water to extension cord ground = 2v
Pool deck to extension cord ground = 2v
Turn off the house main, still reading 2v to ground.
The primary cause here is that the pool contractor did not run a bonding wire to the pool equipment, which means it didn’t connect with the house service via pump wiring EGC, so the spa EGC is electrically isolated from the pool deck.
When I was called in to do the original wiring, the pool was incomplete, but the concrete deck was already poured. The city even back then inspected for bonding, so I don’t know how this got away. I dug all around the equipment pad and did not find a bonding wire.
My plan is to drive electrodes around the pool deck horizontally to the shell of the pool and connect all of them back to the house service.
I also spoke with utility engineer, they might investigate the source. No definitive yes on that yet.
Sent from my iPad using Tapatalk
I did the wiring installation for the hot tub 14/yrs ago while the pool was still under construction. The original HO worked for the tub manufacturer, which is why they didn’t do a built in spa.
Anyway, new HO calls me, they feel voltage entering and exiting the spa. They’ve lived here 4/yrs and this just started.
Here are pics of install


I.


Pool water to pool deck = 0v
Pool deck to stairs = 0v
Spa water to stairs = 2v
Spa water to extension cord ground = 2v
Pool deck to extension cord ground = 2v
Turn off the house main, still reading 2v to ground.
The primary cause here is that the pool contractor did not run a bonding wire to the pool equipment, which means it didn’t connect with the house service via pump wiring EGC, so the spa EGC is electrically isolated from the pool deck.
When I was called in to do the original wiring, the pool was incomplete, but the concrete deck was already poured. The city even back then inspected for bonding, so I don’t know how this got away. I dug all around the equipment pad and did not find a bonding wire.
My plan is to drive electrodes around the pool deck horizontally to the shell of the pool and connect all of them back to the house service.
I also spoke with utility engineer, they might investigate the source. No definitive yes on that yet.