Customer wants a 150a. Lincoln Welder hooked up. 1 phase 208v. The specs in the book for the welder shows 150 amp Inverse Time or Thermal/Magnetic circuit breaker or (Super Lag) Fuses. They have a Cutler Hammer pnl with space if cutler hammer made a 150amp breaker that could fit in 3-one inch spaces, but they dont. The breakers stop at 100amps for the 3-one inch spaces. My plan was to install a 150amp breaker (if they made it) , then install a disconnect with 150amp TD fuses. Finding that this is not an option, some suggestions would be great..
Another question would be do they make a flexible cord rated at 150amps, like an SO cord? I'm picturing something like a 50amp scatter box cord, only rated for 150amps. This would be from the disco to the welder. The welder came with a two screw connector attached right out the box, and its on wheels.
I'm close to calling the customer and telling him to down size his welder.. Suggestions anyone?
Another question would be do they make a flexible cord rated at 150amps, like an SO cord? I'm picturing something like a 50amp scatter box cord, only rated for 150amps. This would be from the disco to the welder. The welder came with a two screw connector attached right out the box, and its on wheels.