newservice
Senior Member
Customer has older house with plaster walls, has 2 old (yes k&t vintage) unswitched sconces on a wall that they are going to make into a library with a nice full wall book shelf to be constructed. Shelfs are probly 10" wide. The proposal so far is to cut holes in the back panel of the shelf where the sconces are now, J box, and extend on NM 14ga. to a removable blank panel on the front and mount the new sconces. My question, does this pass the smell test? I think I'm ok with J box inside the removable panel being visible and accessable, after all if you take the panel off its visible.
I'm more concerned with using romex in the book case; is the case now part of the structure, etc...knowledgeble comments appreciated...:angel: