ToxWat
Member
- Location
- Austin, TX
I just looked at a Cutler Hammer sub-panel that was installed about 2 years ago. The workmanship looks good. The panel is stuffed full of AFCI and GF/AFCI breakers. All of the breakers are hot, not warm, HOT. The ambient temp in the garage was 98F but the surface temperatures of all of the breakers ranged from 120F at the bottom to 170F at the top. I measured the feeder current at 3 amps on the A phase, and 6 amps on the B phase so the heat cannot be caused by excessive current. I was brought in to check the dish washer circuit which trips and won't reset. I verified the branch circuit is clear. The home owner said this is the 2nd breaker to fail. I noticed that most of the breakers with neutral pigtails were discolored where they exit the breaker frame. I know a lot of people will space out AFCI breakers because of heat, but this panel has all AFCI, GFCI, or GF/AFCI breakers except for 2 which ironically are at the bottom. I've looked to see if there has been a recall or if anyone else has experienced this and have come up empty. A penny for your thoughts?