Cutting neutral and 220ing shared circuit
Hi I was hoping someone could explain to me how when you are sharing a neutral on a branch circuit and you cut that neutral without deenergizing the shared circuit why are you susseptable to backfeeding on the other ungrounded conducter. I understand that it happens I just don't understand the technical reason why.
infinity
New Jersey
Journeyman Electrician
It's because the two loads are now in series and each load will see a different voltage drop across it based on it's resistance. The current will be the same through both loads. Two equal loads will share the total voltage equally. For a 208 volt system two identical loads will have 104 volts across them. For a 240 volt system the two loads will have 120 volts across them.
chris kennedy
Miami Fla.
60 yr old tool twisting electrician
Power is going into the shared circuit. It will travel through a load and look for a return path to the source. Hence, energized grounded conductor.
nakulak
draw it out on a piece of paper
plug on left is fed from left with a phase
in middle is juction box with neutrals
plug on right is fed from right with b phase
cut neutral going to panel, and you have a phase on left plug, former neutrals connecting the two plugs are now just a jumper, and b phase on right, so now you have the two plugs fed with 220. make sense ?