Cutting Out Junction Boxes

Status
Not open for further replies.

Dynamite

Member
Is there anything in the NEC which doesn't allow you to cut out the back of a junction box to allow a group of conduits to enter the box. In my example, I have three conduits turned out of a masonry wall and I cut a hole in the back of the junction box to allow the conduits to enter. We grounded the conduits to the box with a ground tail. The inspector is telling us this is not acceptable and that the conduits must be physically connected to the box. Any NEC references you could provide would be greatly appreciated.
 
300.12 Mechanical Continuity ? Raceways and
Cables. Metal or nonmetallic raceways, cable armors, and
cable sheaths shall be continuous between cabinets, boxes,
fittings, or other enclosures or outlets.

Exception No. 1: Short sections of raceways used to provide
support or protection of cable assemblies from physical
damage shall not be required to be mechanically
continuous.

Exception No. 2: Raceways and cables installed into the
bottom of open bottom equipment, such as switchboards,
motor control centers, and floor or pad-mounted transformers,
shall not be required to be mechanically secured to the
equipment.
 
Cutting Out Junction Boxes

Does this actually mean the conduits have to be physically fastened to the junction box, or just that they can't be separated anywhere between the boxes? Doesn't the ground wire satisfy the continuity requirement?
 
300.12 Mechanical Continuity ? Raceways and
Cables. Metal or nonmetallic raceways, cable armors, and
cable sheaths shall be continuous between cabinets, boxes,
fittings, or other enclosures or outlets.

Exception No. 1: Short sections of raceways used to provide
support or protection of cable assemblies from physical
damage shall not be required to be mechanically
continuous.

Exception No. 2: Raceways and cables installed into the
bottom of open bottom equipment, such as switchboards,
motor control centers, and floor or pad-mounted transformers,
shall not be required to be mechanically secured to the
equipment.

I always love implied standards [sarcasm]. Note the main body of this article subsection does not say raceways and cables must be mechanically connected to the box and such, but rather they must be continuous "between" boxes and such. It is only Exception 2 which implies the main body should be interpretted as meaning connected to the box.
 
Does this actually mean the conduits have to be physically fastened to the junction box, or just that they can't be separated anywhere between the boxes? Doesn't the ground wire satisfy the continuity requirement?
There are two rules....300.12 for mechanical continuity and 300.10 for electrical continuity. You have to comply with both.
 
Not to be to critical, but as an inspector that just makes it look like you didn't plan your job out to well or you were just trying to make it "work".

Inspectors see things like that and they start looking real hard at the rest of the job. It just doesn't build a lot of confidence.

Now I will admit that it would have taken me a little time to find a code violation for it.
 