I couldn't find in the search area of the forum if this has been discussed so sorry if this has come up before. The contractor is cutting out a large hole in the bottom of several panels on the job to accomodate the entry of conduits. I tried to explain that transformer, switchboards, switchgear is designed to have open bottoms but panels are not designed to have the bottoms cut out. There is no exposed opening you can put your hand up in. The panel is mounted on a trough that has the identical hole cut in it as well. I also tried to cite code sections
110.12 Mechanical Execution of Work
110.12(A) Unused Openings
300.10 Electrical Continuity of Metal Raceways and Enclosures
300.13 Mechanical and Electrical Continuity
But the contractor says they are not violating any code reference
110.12 Mechanical Execution of Work
110.12(A) Unused Openings
300.10 Electrical Continuity of Metal Raceways and Enclosures
300.13 Mechanical and Electrical Continuity
But the contractor says they are not violating any code reference