I had installed a UPS in one of our older communication site last week. The cabinet, maint. by pass switch, output disconnect and power modules were removed from another building and we "acquired" it. Every thing taken out neatly no problem. I had every thing wired and ready to go. My new battery packs came in and I went to start it up. Got every thing going, moved the switch to UPS and boom main breaker trips UPS shuts down on "Phase Short". What the hell. Take every thing apart to start checking all wiring, this is only about the 50th UPS like this I have installed so I'm not a virgin.
Start ohming out the wires. When I checked the UPS output to the switch it showed the phases were crossed. Doesn't matter that its a single phase unit they do not like the phases crossed. So I check from UPS to bottom side of the output disconnect, a Cuttler-Hammer 125 amp 25 kACI breaker, every thing fine. Check from top of breaker to switch, good. Check from bottom of breaker to switch phases crossed. Start looking at the breaker and find on the underside of breaker, toward the back was a sticker showing the phases are X'ed. This breaker mounts in the enclosure horizontally with the lugs on top and bottom, switch to the left is closed, to the right is open. The top left lug is common to the bottom right lug and the top right lug is common to the bottom left. What kind of crap is that. The breaker crossed phases for me. I guess under normal circumstances it wouldn't matter but these UPS just don't like it.
That's why I buy fusible disconnects for our new installs. Hate working with used crap.
Start ohming out the wires. When I checked the UPS output to the switch it showed the phases were crossed. Doesn't matter that its a single phase unit they do not like the phases crossed. So I check from UPS to bottom side of the output disconnect, a Cuttler-Hammer 125 amp 25 kACI breaker, every thing fine. Check from top of breaker to switch, good. Check from bottom of breaker to switch phases crossed. Start looking at the breaker and find on the underside of breaker, toward the back was a sticker showing the phases are X'ed. This breaker mounts in the enclosure horizontally with the lugs on top and bottom, switch to the left is closed, to the right is open. The top left lug is common to the bottom right lug and the top right lug is common to the bottom left. What kind of crap is that. The breaker crossed phases for me. I guess under normal circumstances it wouldn't matter but these UPS just don't like it.
That's why I buy fusible disconnects for our new installs. Hate working with used crap.