Do I need to derate cables for conduit fill (80% for three or more) for D.C. battery banks? Are they considered current carring conductors when its stored power? (i.e. UPS batteries) I can see the logic for A.C. with the field creating heat issues. But I'm not sure with dc.
True. But it does make a difference to voltage drop. It isn't particularly significant for smaller cables but can be a consideration for larger cables.Current passing through resistance creates heat. It doesn't matter whether that current is direct or alternating.
True. But it does make a difference to voltage drop. It isn't particularly significant for smaller cables but can be a consideration for larger cables.
For 300 mm^2 (no exact conversion but it would be about the conductor size as 600 kcmil if you had such a thing) the difference in voltage drop from DC to AC is about 30%.
I'm as enigmatic as Mona Lisa's smile.I've got a lot of these guys figured out, but I'm still working on you.![]()
The lamp will have equal brightness on 100Vdc or 100Vac rms.Heres why dc remains lets say at 100 volts constant whereas ac voltage reaches 100 volts at two points during the cycle in order for the lamp to light with equal brilliance on ac to dc we must raise the ac voltage to 141 volts.
The thermal inertia
Learning new stuff here is a no-cost option.Now theres a term I have never seen used before.![]()
The lamp will have equal brightness on 100Vdc or 100Vac rms.
The rms is the effective value. 141V is the peak.
The thermal inertia of an incandescent lamp is usually sufficient to avoid discernable flicker.