6 618electrician New User Location St. Louis Occupation Maintenance electrician Feb 12, 2025 #1 In the 2020 nec can you daisy chain receptacles ? ( no wire nuts ) 120 volt 15 amp outlets ???????????????
In the 2020 nec can you daisy chain receptacles ? ( no wire nuts ) 120 volt 15 amp outlets ???????????????
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 12, 2025 #2 Yes, the only place where you may need to splice is with a MWBC. Welcome to the Forum.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 12, 2025 #3 Yes unless you are dealing with the neutral on a MWBC Opps posted on top of rob)