But you can't daisy chain with a whip (assuming we are talking about the typical whips with 18 gauge conductors)If the troffers are close together where you can daisy chain with a whip of 6' or less, you can install these whips unsupported if you use listed connectors. The NEC considers the connectors as adequate support. If they are further apart, I like to run EMT and use a J box and have 3 or 4 whips to the fixtures. The same 6' rule applies to these whips from a J box.
Correct, you would need branch circuit sized conductors and a wire type EGC.But you can't daisy chain with a whip (assuming we are talking about the typical whips with 18 gauge conductors)
Once I saw a fixture whip in the beginning of a daisy chain of good 15-16A worth of troffers, it was a bit warmCorrect, you would need branch circuit sized conductors and a wire type EGC.
I agree. If we daisy chain, the circuit conductors must have the ampacity of the branch circuit rating. Thanks for the added input.But you can't daisy chain with a whip (assuming we are talking about the typical whips with 18 gauge conductors)
Because the 14 would be a branch circuit conductor and you can't have taps on branch circuits. The conductors in the whip are fixture wires and 240.4(E)(2) refers you to 240.5(B)(2) for the overcurrent protection of fixture wire.On a side note, in a residential setting where the local codes do not permit #14 wire and 15 amp circuits for power and lighting, I have seen electricians pull #12 feeds in and out of switch locations but pull #14 switchlegs to lighting outlets. The inspectors turn them down for this because they consider the smaller switchleg a "tap" conductor. How is this any different than using a smaller conductor for a troffer in a whip?
Can you still have a tap on a branch circuit supplying a counter mounted cooking unit and and a cabinet mounted oven? I think I remember that in one of the notes of T.220.55. But I think it's the only place on a branch circuit that allows tap conductors? Thank you for the response.Because the 14 would be a branch circuit conductor and you can't have taps on branch circuits. The conductors in the whip are fixture wires and 240.4(E)(2) refers you to 240.5(B)(2) for the overcurrent protection of fixture wire.
It seems strange that you can't use 14 THHN in an application where you can use 18 TFFN, but that is what the code says.
Even if you make your own whips, you would have to use wire sized to the branch circuit OCPD, unless you used fixture wire to make the whip.
See 210.19(B) Exception 1Can you still have a tap on a branch circuit supplying a counter mounted cooking unit and and a cabinet mounted oven? I think I remember that in one of the notes of T.220.55. But I think it's the only place on a branch circuit that allows tap conductors? Thank you for the response.