System:
A 69 kv line feeding a privately owned substation with a ABB switch which feeds a 8MV 69kv to 12470 KV transformer that steps the power down to 15 kv which feeds three single phase voltage regulators which then connect to a 15kv overhead bus duct which then connects to a 15 kv breaker/switch which feeds a 15KV line up which feeds 6-15kv to 480/277 volt transformers
The problem: The 15 KV overhead inclosed bus duct shorted out and the up stream ABB breakers batteries were dead so it did on sense the fault. The power companies rirst up stream substation fuse did not sense the fault, the second upstream substation did sense the fault and shut the overhead line off.
The Damage: The 8 MV transformer was distroyed and the bus duct was distroyed along with the incomming section of the 15kv switch. We replaced the 8 mv transformer all of the cables and the 15kv bus duct, the incomming section of the 15 kv switch/breaker and had all items tested. Had the batteries and charger replaced on ath ABB switch and the settings confirmed and tested. Tested all of the cables to the 15 kv lineup and they were fine.
Tested all of the downstream transformers and they were fine. turned everything on and everything was fine. At the time it was noted by the Eaton testing person that the highes fault was on the A phase recorded at the 15 kv switch (logged in the memorly. This all happened in December of last year.
Current issue: We got called out by the same customer due to a feeder short on one 4000 amp MDS switchboard #1 which also feeds a motor control center phase A in one of the 11 feeders on the switchboard went to ground to phase C, the same thing happened on the 1200 amp mcc. Seems odd to me. Is there any way that the high fault current recorded on the 15 kv switch worked its way downstream. Any thoughts\
Thanks in advance
A 69 kv line feeding a privately owned substation with a ABB switch which feeds a 8MV 69kv to 12470 KV transformer that steps the power down to 15 kv which feeds three single phase voltage regulators which then connect to a 15kv overhead bus duct which then connects to a 15 kv breaker/switch which feeds a 15KV line up which feeds 6-15kv to 480/277 volt transformers
The problem: The 15 KV overhead inclosed bus duct shorted out and the up stream ABB breakers batteries were dead so it did on sense the fault. The power companies rirst up stream substation fuse did not sense the fault, the second upstream substation did sense the fault and shut the overhead line off.
The Damage: The 8 MV transformer was distroyed and the bus duct was distroyed along with the incomming section of the 15kv switch. We replaced the 8 mv transformer all of the cables and the 15kv bus duct, the incomming section of the 15 kv switch/breaker and had all items tested. Had the batteries and charger replaced on ath ABB switch and the settings confirmed and tested. Tested all of the cables to the 15 kv lineup and they were fine.
Tested all of the downstream transformers and they were fine. turned everything on and everything was fine. At the time it was noted by the Eaton testing person that the highes fault was on the A phase recorded at the 15 kv switch (logged in the memorly. This all happened in December of last year.
Current issue: We got called out by the same customer due to a feeder short on one 4000 amp MDS switchboard #1 which also feeds a motor control center phase A in one of the 11 feeders on the switchboard went to ground to phase C, the same thing happened on the 1200 amp mcc. Seems odd to me. Is there any way that the high fault current recorded on the 15 kv switch worked its way downstream. Any thoughts\
Thanks in advance