Damaged Wire in Conduit
StarCat
Industrial Engineering Tech
Moab, UT USA
Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
I have dealt with this a few times over the years, and its been difficult except when there is an obvious direct short.
I have another instaance where this may be the case, and may not have access to a Mega Ohm device for any kind of test of said wire.
This is a 3PH-208V service to a 7.5 HP reciprocating air compressor, and there are some known offenders with the machinery itself which can cause the same symptoms of random and unexplained breaker trips whch can also sometimes be hard to nail down. The Mechanic comes around, RESET and everything gives normal readings, sights, and sounds. The known offenders on the machine do not come as suspect in this case. Its a classic Ghost setting.
This is also a case of having solid core wire ont he original pull and a lot of magnetic repulsion on start up heard in the conduit historically. All with starting and running current in the normal range. The last time I came across this problem and identified it for sure was on a 480V 3 PH system, and there was an intermittent arc to ground that could be seen from the end of a conduit run. In this case I am never around when the fault happen.
Would a MEG test in such a case likely be conclusive ?
Any advice is helpful.
Star
I believe a meg test would give an answer however if you don't have a meg and you have another motor, then I would switch it out and see if the same issue occurs...
Dennis Agreed, and this did occur to me as I do happen to have an exact twin next to it.
Ret, this has been done. Unable to catch any misbehavior when I am starting the system.
We had a customer that we did yearly downtime checks of motors. One megged odd. Sure enough vibration at the peckerhead had worn thru the insulation of one of the wires. Never stuck long enough to blow a breaker in this case. It would help to have a yearly base line to compare with, but you have to start somewhere.