hello,
so im sure everyone is familiar with the "sim pull" technology for single insulated conductors, and im sure many have scuffed it up. Am i wrong to think that the most outer, clear part of the jacket is strictly for the sim pull purpose? I managed to peel some back while pulling thhn/thwn-2 4/0 wire, 200 ft run. The wire still passed the megger with 4000m ohms. I am looking to see if anyone can see a reason why the wire would need to be replaced, possibly if that part of the insulation has something to do with moisture protection. I noticed the local inspector feeling the damage as well. I can try to add photos if necessary but im assuming it is clear what I am talking about.
so im sure everyone is familiar with the "sim pull" technology for single insulated conductors, and im sure many have scuffed it up. Am i wrong to think that the most outer, clear part of the jacket is strictly for the sim pull purpose? I managed to peel some back while pulling thhn/thwn-2 4/0 wire, 200 ft run. The wire still passed the megger with 4000m ohms. I am looking to see if anyone can see a reason why the wire would need to be replaced, possibly if that part of the insulation has something to do with moisture protection. I noticed the local inspector feeling the damage as well. I can try to add photos if necessary but im assuming it is clear what I am talking about.