ishium 80439
Senior Member
Would a piece of EMT installed on the exterior of a home using raintight fittings be considered a damp location? (Well, I guess I mean inside the conduit, not the EMT itself):grin:
Would a piece of EMT installed on the exterior of a home using raintight fittings be considered a damp location?
So let me take this a step further. If you install a surface mount weatherproof box fed through the wall and use NM to feed, say, a GFI, does that mean that installation is in violation because you are using NM in a wet/ damp location?
So let me take this a step further. If you install a surface mount weatherproof box fed through the wall and use NM to feed, say, a GFI, does that mean that installation is in violation because you are using NM in a wet/ damp location?
His question was not about entering the back of the box,,,it was talking about nm in conduit.
Sorry if I caused confusion. I'm just trying to figure out consistency. If NM is illegal in exterior conduit, and when it is stripped out it has no rating (and therefore is not in compliance) than doesn't that mean that you can't have NM enter the back of an exterior box? And to go further doesn't that mean that exterior panels would also be in violation?
I may be missing something but I didn't see anything in 334 to the effect of "damp/ wet locations as long as the cable terminates in that box". If once it is outside it is a wet location and it is not allowed in a wet location than it seems to me that there are oodles of non-compliant work out there that has been signed off on as OK.
When a conduit is buried IT CONDENSATES. I've heard of guys saying "if you use primer and then glue, the PVC will be dry,,,,BOLONY,,,it doesn't matter if you use primer then glue,,,,ALL UNDERGROUND PVC is wet inside.Worse than consistency, I'm about to look for practicality. What is the arguement that NM is good in a weathertight enclosure (ie panel, box etc)Here is the actual situation I've encountered: We relocated a panel around the corner from it's original location- linereally it's about 6' away from where it was. We mounted a trough at floor joist height, brought all of the BC's into the trough and passed them through 2" offset nipples into the panel and terminated directly to the panel. It seems (I've not yet talked to him personally, just going by the correction notice and what the GC said) that he is saying that coming into the gutter is fine, but once we pass through the nipples we have a violation. I'm trying to find out how others would view this.HTML:but not a weather tight conduit? It seems all out or all in.
As an aside, from a quality perspective, it's my opinion that the installation as is, is a better solution than putting a million splices in the gutter just so we can run the final 2' in THHN.
Other thread... said:Excellent point, and no I have never been hit on that.... IMO if you were going to get hit on that - you should also be hit on that for taking them to an exterior panel in the first place. So I see no difference in taking them to a box first then a short distance to the panel. Others may disagree... But otherise you are almost forced to use a large KO, as often that is what is given on the back of most panels - often leaving very little space for much else... That one could secure correctly. And the cable jacket, and its conductors are still outside - be it in a cabinet or a J-bx. If you're getting hit on that - then everyone should be bringing UF out any exterior panel - right?When coming up in the trade in CT I never saw a panel installed w/ the chase nipple method. Than again I don't think I ever saw an exterior loadcenter. Here in CO it is the norm to have an exterior loadcenter and the chase nipple method is prevalent in the entire metro area. When one is doing a service upgrade there is really not a whole lot of choice but to replicate the same method (unless you are willing to do lots of damage to the interior finishes. I see lots of new work still being done this way but I've never really liked it. On new work I always put the panel inside and enter via the methods discussed (I've never really understood why people like the panels outside).
E57, if I understand your description, you set a box, drop the EGC's and turn the other conductors through a nipple and terminate them in the panel. Isn't this a violation by having the stripped NM in exterior conduit? The reason I ask is I have a thread going where I did something similiar (brought the NM into a trough and turned the conductors up through 2" chase nipples) and was shot down for the conductors being in a wet location.
Sometimes you have to break some eggs - and I'll be happy to say that in the other thread too.
Up to interpetation IMO.... Pretty vague....334.12(B)4 in the '05 NEC said:Where exposed or subject to excessive moisture or dampness
:roll: That could getcha... But IMO if they choose to enforce that - then all exterior panels need to have UF cable or some other wet/damp location rated wire or cable - just to get into a box or cabinet. For that matter into any exterior light fixture, or even still - any damp location, say a bath fixture....334.12(B)4 in the '08 NEC said:In wet or damp locations.
Can someone point to where the conduit, or J-bx or cabinet requires the conductors be of a certain type? Except for conduits underground etc, the inside of conduits could only ever be at worst a damp location....
Sorry buddy both of those stated are not in MY code book... I'm still on the '05300.9 states that the interiors of raceways installed in wet locations above grade shall be considered wet locations. It also says insulated conductors in said raceways shall comply with 310.8(C), which lists the characteristics and types of insulation.
It should give a ruling on conductors in enclosures in wet locations above grade, but doesn't.