steveng said::-? what is a dash pot used for?
is a magnetic underload relay the same as a dashpot?
i have some at work, they are used on a lighting control circuit.
mdshunk said:The only dashpots I know about are little shock absorbers used in motion control applications to prevent overrun from damaging equipment.
jim dungar said:Oil-filled dashpot "time-delay" overload relays were not un-common on both circuit breakers and motor starters. They were difficult to regulate (set the time delay) and required regular maintenance of their oil level.
Static trip devices (electronic) replaced dashpots in the early to mid 60's, although some old equipment is still in service.
Jraef said:They were pretty much replaced first by eutectic melting alloy relays (a.k.a. solder pot relays), then again by bimetallic thermal relays, now by solid state current sensing relays. Don't re-use them, you can get in trouble from the hazmat people.
I put in a few in the early 70s as part of a relay control schemes. Some were additions to a contactor to slow it dropping out - called "tail-piece timers. Prevented relay races in control systems.steveng said:...this dashpot coil is 277v and the relay contact is feeding a 1 kva xfmr
pri 277 and sec 120/240. ...the lighting contactor is 4 poles 277v, 2 of the circuits are from and emergency generator, for lighting.
Jraef said:Dash pot relays were often used as overload relays that would provide a delayed reaction to an instantaneous current surge, but eventual tripping if the increased current continued for a time. There was a heater coil in a pot containing oil, the heated oil would expand and flow through an orifice to a plunger that would eventually trip a spring loaded contact. If the current went down and the heater coil cooled off, the oil would flow back into the pot. You could change the delay time by using an oil with a different viscosity, usually designated by color. So for example if you wanted a 10 second delay, you used a red oil, 20 seconds was a green oil etc. etc. (I don't really remember the color codes and values any more, that was 30+ years ago for me). They stopped using them in the late '70s because the dashpot oil had PCBs in it and was highly flammable if it leaked. Most likely on a lighting transformer system it was used to prevent long term overloading of the transformer, but allowed temporary overloading as HID ballasts were striking at the beginning of the day.
thanks for the explanation, after looking closer at this, i can see you are right,
this application was used to bring on some 120v lights that are in a stairwell,
that are next to hid fixtures 277, the incandescent lights were on instant, and delayed off, allowing the hid fixtures to reach full brightness. the dashpot was connected to a relay contact that is feeding the primary 277 to a .250kva xfmr, which powers the 120 incandescent lamps, there are only 3 120v lamps per stairwell, in a 2nd floor bldg.
makes good sense now, thanks, i appreciate the help i receive here