data and fire alarm cable in same bridle rings

Status
Not open for further replies.

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Ive looked and cannot find this question. Can i run data and fire alarm cable in the same bridle rings?

Yes, as long as:

1. The fire alarm cable is power limited (Class 2 or Class 3 source)
2. There is no local amendment prohibiting this (check with the AHJ/building departemnt)
3. There is no restriction in the specifications or on the drawings regarding co-location of these cable types.
 