Data and Power Cables In Same Access Hole

Status
Not open for further replies.

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Not sure exactly what you are asking so I'll attempt to answer both interpretations.

You can't run data in the same duct or raceway with power unless the power is a listed cable.

If the power is by itself in it's own duct or raceway then there should be no problem with that raceway sharing a hole with LV data.

-Hal
 