I am building a retail facility and have been asked to have the electrician run a coaxial cable and a romex cable in the same conduit (drop pole) that hangs from the ceiling and supports the TV monitor. The ceiling junction box does have a separation for power from data. Does having the power and data together like this in the drop pole violate the NEC? Would it matter if the power cable was MX?
 

celtic

Senior Member
Location
NJ
Re: Data and Power in One Conduit

Originally posted by bobgossman:
...run a coaxial cable and a romex cable in the same conduit (drop pole).
What are we talking about here?
A conduit/pipe?
Or a "power pole?

Originally posted by bobgossman:

Does having the power and data together like this in the drop pole violate the NEC? Would it matter if the power cable was MX?
In a conduit = violation.
In a power pole approved for power/data (will have a barrier) = no violation

I have no idea what "MX" is, do you mean "MC"?

Originally posted by bobgossman:

I am building a retail facility ..
RX in retail?
That's probably a violation , also. (334.12(A)(1)~ 2002 NEC)


This is a power pole:
telepower.jpg

See: Wiremold Tele-Power pole

EDIT: Linked back to image..oops.

[ January 28, 2006, 04:08 PM: Message edited by: celtic ]
 
Re: Data and Power in One Conduit

The conduit hangs from the ceiling, supports a TV monitor, and does not touch the floor. It does not have receptacles mounted in it. It is not a power pole. You have probably seen these TV monitors advertising merchandise in big box stores.

I meant MC cable, not MX.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Data and Power in One Conduit

I would do it with MC and not even think about it.

The 'conduit' is not a raceway, it is a support pole. ;)

MC and Coaxial cable are both cables that do not require raceways and are allowed to be fished into hollow spaces.

IMO running them both in this support pole is no different then running them both in the same stud bay.

IMO using NM would likely cause interference on the coax.
 

jimwalker

Senior Member
Location
TAMPA FLORIDA
Re: Data and Power in One Conduit

Sounds like it is a structure to hold the TV.As long as the receptacle and its box are mounted on the outside of this pole i think its ok.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Data and Power in One Conduit

Originally posted by pierre:
820.133(A)(2)ex. # 1 would permit this type of installation.
Pierre if we call this support pipe a 'raceway' we cannot hang the TV from it.

IMO the exception you point to does not apply as this pipe is not a raceway it is just a hollow void that the cables can be snaked through.
 

bully

Member
Re: Data and Power in One Conduit

Data and power can run in the same conduit if you use simtra cable. It comply with NEC and is UL approved. Power conductor is insulated with a barrier that shielded the EMI. I use it all the time in the same conduit with data, voice or phone. They also have outlet boxes with combination of power, data and phone. It's very ease to work with and just one pulling. Let me know if you need more information.
 