Short version: Does a data center, built to 1996 NEC code, need to have a mushroom-type EPO button, or does a readily-accessible main breaker in a panel qualify as an approved disconnecting means?
Long version:
I've got a small data center that I've recently been doing some upgrades to (mostly pulling Cat5/6 and fiber).
There was a brief power outage (confirmed it was a utility problem) that took down the whole room.
Since I'm here, I was asked to have a look at things to see why it happened.
The data center is powered by an ancient UPS battery system. I've determined that that system failed and needs to be replaced, as it did not protect their equipment from the outage. Up to the client whether they want to or not.
Now to my question, I noticed that the data center room itself does not have an Emergency Power Off (EPO) button anywhere. There is a shunt trip on the main breaker to the room, but it's not hooked up to anything!
Also, the UPS room/battery room has an EPO, but it's a keyswitch, not a mushroom button like I usually see. Also, the key is missing...
This is in New York City, so 2008 NEC currently. I've read through Art 645, 685, and NFPA 75 (75-2009 is the earliest I could find), the requirement for "disconnecting means" is pretty vague - seems to be up to the AHJ inspector. The systems were installed in 1999, and last upgraded (but not replaced) in 2002. I believe the 1996 NEC was current in NYC at the time the room was installed, so I've read that version too.
The 1996 NEC, Art 645.10 says "A means shall be provided to disconnect power to all electronic equipment in the information technology equipment room. ... The control for these disconnecting means shall be grouped and identified and shall be readily accessible at the principal exit doors."
Hoping someone here who does power wiring to data centers could weigh in on this. Is the data center room required to have an EPO button installed given that it was built in 1999 (1996 NEC) or does the main breaker in the panel satisfy the requirement? (The panel is within a few feet of the door.) If it must be a separate switch/button, can the EPO in either the data center or the UPS room be a keyswitch, or must it be a single-action mushroom type? Does the EPO in the data center have to disconnect the batteries in the UPS room as well, or can it just trip the main breaker, after the ups? (The EPO in the UPS room must disconnect the batteries, as I read it.)
Thanks.
(Sorry if this double-posts, got logged out while typing.)
Long version:
I've got a small data center that I've recently been doing some upgrades to (mostly pulling Cat5/6 and fiber).
There was a brief power outage (confirmed it was a utility problem) that took down the whole room.
Since I'm here, I was asked to have a look at things to see why it happened.
The data center is powered by an ancient UPS battery system. I've determined that that system failed and needs to be replaced, as it did not protect their equipment from the outage. Up to the client whether they want to or not.
Now to my question, I noticed that the data center room itself does not have an Emergency Power Off (EPO) button anywhere. There is a shunt trip on the main breaker to the room, but it's not hooked up to anything!
Also, the UPS room/battery room has an EPO, but it's a keyswitch, not a mushroom button like I usually see. Also, the key is missing...
This is in New York City, so 2008 NEC currently. I've read through Art 645, 685, and NFPA 75 (75-2009 is the earliest I could find), the requirement for "disconnecting means" is pretty vague - seems to be up to the AHJ inspector. The systems were installed in 1999, and last upgraded (but not replaced) in 2002. I believe the 1996 NEC was current in NYC at the time the room was installed, so I've read that version too.
The 1996 NEC, Art 645.10 says "A means shall be provided to disconnect power to all electronic equipment in the information technology equipment room. ... The control for these disconnecting means shall be grouped and identified and shall be readily accessible at the principal exit doors."
Hoping someone here who does power wiring to data centers could weigh in on this. Is the data center room required to have an EPO button installed given that it was built in 1999 (1996 NEC) or does the main breaker in the panel satisfy the requirement? (The panel is within a few feet of the door.) If it must be a separate switch/button, can the EPO in either the data center or the UPS room be a keyswitch, or must it be a single-action mushroom type? Does the EPO in the data center have to disconnect the batteries in the UPS room as well, or can it just trip the main breaker, after the ups? (The EPO in the UPS room must disconnect the batteries, as I read it.)
Thanks.
(Sorry if this double-posts, got logged out while typing.)