Do you have to use plenum rated wire under a data center raised floor?
C cbryull New member Jul 7, 2005 #1 Do you have to use plenum rated wire under a data center raised floor?
dereckbc Moderator Staff member Location Plano, TX Jul 7, 2005 #2 Re: Data Centers Raised Floor Is it article 645 compliant?. If yes, then no. If no, then yes. [ July 07, 2005, 04:41 PM: Message edited by: dereckbc ]
Re: Data Centers Raised Floor Is it article 645 compliant?. If yes, then no. If no, then yes. [ July 07, 2005, 04:41 PM: Message edited by: dereckbc ]
ron Senior Member Location New York, 40.7514,-73.9925 Jul 7, 2005 #3 Re: Data Centers Raised Floor Now that Dereck edited the Article number, I agree with him
dereckbc Moderator Staff member Location Plano, TX Jul 7, 2005 #4 Re: Data Centers Raised Floor Ya, I know, having a bad typo day.