Is there any way to get a utility to provide information so that NFPA70E can be followed. Maximum fault values are not sufficient for performing arc-flash calculations.
If the primary side is so dynamic that it is unpredictable, why can't they simply provide maximum and actual fault current and X/R values at the secondary of the transformer? That data would be steady, until the transformer is replaced.
An engineered (like IEEE 1584) arc-flash study can take into the fact the utility will never clear the fault. The customer can then deal with the fact no PPE is adequate for service entrance equipment. But, without valid information from the utility (the same data the utility uses for their own calculations) it is not possible to determine the actual fault levels at other locations in the facility.
A local POCO says they do not believe in any engineered arc-flash study and advises their customers to simply follow the tables in NFPA 70E. But, the first note to the tables says the information is only valid for "25kA short circuit available, .03 second (2 cyle) fault clearing time". What is the customer to do when they are told the maximum [future] fault level is 57kA?
If the primary side is so dynamic that it is unpredictable, why can't they simply provide maximum and actual fault current and X/R values at the secondary of the transformer? That data would be steady, until the transformer is replaced.
An engineered (like IEEE 1584) arc-flash study can take into the fact the utility will never clear the fault. The customer can then deal with the fact no PPE is adequate for service entrance equipment. But, without valid information from the utility (the same data the utility uses for their own calculations) it is not possible to determine the actual fault levels at other locations in the facility.
A local POCO says they do not believe in any engineered arc-flash study and advises their customers to simply follow the tables in NFPA 70E. But, the first note to the tables says the information is only valid for "25kA short circuit available, .03 second (2 cyle) fault clearing time". What is the customer to do when they are told the maximum [future] fault level is 57kA?