Hello all,
I have a 400 Hz generator that has an output of "72 amps continuous" as actually labeled on the data plate. My question is should I install wire/OCPD for 90 amps (72 x 1.25) or is this the max continuous amperage already calculated on the data plate (57.6 x 1.25 = 72)?