B bartongr Member Jan 9, 2004 #1 What does the 2002 NEC say about runing lighting and data condutors in the same raceway/power pole. Thanks bartongr
What does the 2002 NEC say about runing lighting and data condutors in the same raceway/power pole. Thanks bartongr
iwire Moderator Staff member Location Massachusetts Jan 9, 2004 #2 Re: Data/power They need to be in separate raceways. This could be a power pole with separate compartments.
Re: Data/power They need to be in separate raceways. This could be a power pole with separate compartments.