I'm having a difficult time interpreting the NEC when it comes to datacommication racks. Specifically wall racks that will only house POE switches, patch panels, and cable management for Unshielded Twisted Pair CAT5e/CAT6 cables.
Typically we use wall mounted racks for smaller installation. Something like this:
250.96(A) is typically cited as the code section that governs bonding and grounding of racks and enclosures. However, it says that bonding is only required for "[racks] that are to serve as equipment grounding conductors, with or without the use of supplementary equipment grounding conductors".
800.100 also covers datacom bonding and grounding. However it specifically says "The primary protector and the metallic member(s) of the cable sheath shall be bonded or grounded as specified in ".
It would appear that neither of these criteria are being met with racks that are used exclusively for UTP cable installations. This cable type does not have a "sheath" or shield, and does not require grounding. There is therefore no need for a rack to be used as an ECG and therefore would not need to be bonded or grounded.
Is there a code section that I have missed that covers this, and, if not, is my interpretation of the code accurate — is it consistent with how it is normally interpreted?
Typically we use wall mounted racks for smaller installation. Something like this:
250.96(A) is typically cited as the code section that governs bonding and grounding of racks and enclosures. However, it says that bonding is only required for "[racks] that are to serve as equipment grounding conductors, with or without the use of supplementary equipment grounding conductors".
800.100 also covers datacom bonding and grounding. However it specifically says "The primary protector and the metallic member(s) of the cable sheath shall be bonded or grounded as specified in ".
It would appear that neither of these criteria are being met with racks that are used exclusively for UTP cable installations. This cable type does not have a "sheath" or shield, and does not require grounding. There is therefore no need for a rack to be used as an ECG and therefore would not need to be bonded or grounded.
Is there a code section that I have missed that covers this, and, if not, is my interpretation of the code accurate — is it consistent with how it is normally interpreted?