We are currently working with grounding requirements for Data Rooms. These rooms have a copper ground bus installed in each room and we usually have five or six rooms. Technology folks
install a #6 ground that bonds these together along with bonding data cable trays etc. with this ground. We are supposed to ground these bars to the building ground per NEC requirements. We usually run a 4/0 ground from each to the building service ground point. I have ran across a few University technical specifications that allow the bus bars to be connected to building steel. Our take on this is this ground system is really there to eliminate noise on the data circuits in lieu of people protection that this might be an acceptable method. The NEC as we read it isn't very clear in it's requirements for these type grounds. QUESTION-is building steel acceptable for these grounds and would it be acceptable to ground only one of these ground bars since they are interconnected with #6?
Another point that we need some advise on is building steel itself. Large buildings have expansion isolators at various places. How do these isolators affect the continuity of the steel system? Seems like there might be several
building sections that might be at different potential or does the foundation rebar connect it all together.
Thanks for any info you may have.
JB
install a #6 ground that bonds these together along with bonding data cable trays etc. with this ground. We are supposed to ground these bars to the building ground per NEC requirements. We usually run a 4/0 ground from each to the building service ground point. I have ran across a few University technical specifications that allow the bus bars to be connected to building steel. Our take on this is this ground system is really there to eliminate noise on the data circuits in lieu of people protection that this might be an acceptable method. The NEC as we read it isn't very clear in it's requirements for these type grounds. QUESTION-is building steel acceptable for these grounds and would it be acceptable to ground only one of these ground bars since they are interconnected with #6?
Another point that we need some advise on is building steel itself. Large buildings have expansion isolators at various places. How do these isolators affect the continuity of the steel system? Seems like there might be several
building sections that might be at different potential or does the foundation rebar connect it all together.
Thanks for any info you may have.
JB